What is the short circuit capacity of a 72 KVA transformer with a 240V secondary and 3% impedance?

Prepare for the New York City DOB Master Electrician Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Ace your exam today!

To determine the short circuit capacity of a transformer, you first need to understand the concept of impedance and how it relates to the full-load current of the transformer.

The short circuit current can be calculated using the formula:

[

I_{sc} = \frac{V_{secondary}}{Z}

]

where (I_{sc}) is the short circuit current, (V_{secondary}) is the secondary voltage of the transformer, and (Z) is the impedance expressed as a decimal.

  1. Convert the impedance percentage to decimal form: The impedance is given as 3%, which would be used in the calculation as 0.03.

  2. Calculate the full-load current:

First, we need to calculate the full-load current of the transformer. The formula for full-load current (I_load) in Amperes is given by:

[

I_{load} = \frac{KVA \times 1000}{V}

]

In this case, (KVA = 72) and (V = 240),

[

I_{load} = \frac{72 \times 1000}{240} = 300 \text{ A}